I have an existing multifamily, say 100 units, that wants to upgrade each panel and run electric ranges to eliminate gas. The Service is 3 phase. The Ranges are single phase three wire 220, 8000kW.
220.55 says that "where 2 or more single phase are supplied by a three phase ...service...." the calc would look like this (as shown in the Annex D5(A):
Max rages btwn any 2 phases (34) times 2 (68) then use 68 "ranges" in Table 220.55 Column "B" (cause under 8750 watts) for the "61 & Over" Line so: 25,000W & (68 *.75kW =) 51000W for 76,000W, divided by 2 for Single Phase Load (38000W) then times 3 for three phase = Total Electric Range Load on the 3 Phase Service Feeder of 114kW divided by 360 = 316.6 Amps
In the Multifamily Load Cal Option 220.84 though is says Add Electric Nameplate to total (of Gen Lighting & Small Appliances & Fixed Appliances) then use table for over 62 units and multiply by 23%. In this case 8000W * 100 Units = 800,000 *.23 = 184,000W Divided by 360 = 511.1 Amps
Big Difference for the exact same Line Item.
Since in the 220.84 method the Ranges are the same exact ranges and *If they dont exist yet the calc can be the Gen/Appliance loads times 23% then a year from now they add electric ranges and THEN I can use 220.55?
I dont understand if 220.55 trumps 220.84 now, and I can still use the Single to Three Phase electric range calc... or if 220.84 must have the full nameplate. When I can just as easily merely calculate the Service Feeder Load based on 220.84 for everything but the ranges then say Im adding the ranges later for 316 amps and "luckily" I already sized the Service Feeders for those 316 additional amps coming.
220.55 says that "where 2 or more single phase are supplied by a three phase ...service...." the calc would look like this (as shown in the Annex D5(A):
Max rages btwn any 2 phases (34) times 2 (68) then use 68 "ranges" in Table 220.55 Column "B" (cause under 8750 watts) for the "61 & Over" Line so: 25,000W & (68 *.75kW =) 51000W for 76,000W, divided by 2 for Single Phase Load (38000W) then times 3 for three phase = Total Electric Range Load on the 3 Phase Service Feeder of 114kW divided by 360 = 316.6 Amps
In the Multifamily Load Cal Option 220.84 though is says Add Electric Nameplate to total (of Gen Lighting & Small Appliances & Fixed Appliances) then use table for over 62 units and multiply by 23%. In this case 8000W * 100 Units = 800,000 *.23 = 184,000W Divided by 360 = 511.1 Amps
Big Difference for the exact same Line Item.
Since in the 220.84 method the Ranges are the same exact ranges and *If they dont exist yet the calc can be the Gen/Appliance loads times 23% then a year from now they add electric ranges and THEN I can use 220.55?
I dont understand if 220.55 trumps 220.84 now, and I can still use the Single to Three Phase electric range calc... or if 220.84 must have the full nameplate. When I can just as easily merely calculate the Service Feeder Load based on 220.84 for everything but the ranges then say Im adding the ranges later for 316 amps and "luckily" I already sized the Service Feeders for those 316 additional amps coming.