Re: Electric scissor lift in hazardous location
The NEC does not address this. While 500.1 may at first imply Arts 500-504 apply to this equipment, it must be interpreted in light of the definition of electrical and electronic equipment in Section 500.2; i.e., the Articles apply to ?installations? not to portable or transportable (including mobile) equipment. I don?t know of any other NFPA Standard that applies.
The definition in 500.2 does reference the ISA 12 series of standards, but they don?t apply to the class of equipment you refer to. (I have a calculator that is specifically listed for Class I, Division 2, Groups A, B, C, and D. In my opinion the listing is gross overkill for Divsion 2 only.)
The American Petroleum Institute (API) RP540 also has a very brief set of guidelines for portable but not self-propelled equipment.
My personal opinion is the equipment you mentioned may be used in Division 2 locations fairly routinely but I would have someone very familiar with classified location principles to look it over first. With Division 1 locations, I?d want a Nationally Recognized Testing Laboratory (NRTL) to certify it.