From my customer, for whom I installed an EVSE last week. Manufacturer listing says max output is 30A. I assume this would be the max load, correct? Anyhow, here's what's up for comment:
"Had the inspector out a few minutes ago. He wants us to make one change.
The manual says a 40 amp breaker and that's what we have. But the guy said code requires 10% more than expected load. So we have to bump up to a 50 amp breaker.
The tag on the charger says it takes 30A. On the web I find a spec sheet (attached PDF) that says "Input Current 40A Max". So I guess this is a matter of interpretation. And it's the inspector's interpretation that matters."
Anyhow, that varies from 625.21 by 15% if I understand what the inspector thinks he's referring to. Is there any other applicable Code here, or am I misinterpereting max load?
I was not at the inspection, so could not get any clarification.
Thanks for any review comments.
Bob
"Had the inspector out a few minutes ago. He wants us to make one change.
The manual says a 40 amp breaker and that's what we have. But the guy said code requires 10% more than expected load. So we have to bump up to a 50 amp breaker.
The tag on the charger says it takes 30A. On the web I find a spec sheet (attached PDF) that says "Input Current 40A Max". So I guess this is a matter of interpretation. And it's the inspector's interpretation that matters."
Anyhow, that varies from 625.21 by 15% if I understand what the inspector thinks he's referring to. Is there any other applicable Code here, or am I misinterpereting max load?
I was not at the inspection, so could not get any clarification.
Thanks for any review comments.