Hello all,
I am a licensed electrician in Connecticut employed by a chemical plant. We were told to put in a temporary outlet for an electric truck to use for moving loads as a trial. We found a spare 150amp breaker and used this to feed a 480volt outlet. When we plug the charger in all is good. The charger has an 80 amp breaker in it, when we plug the truck into charge the 80 amp breaker trips. Our main breaker is ok. The company is saying we are feeding it with too high of an amperage and that’s the problem. To me this doesn’t make sense, the way I see it doesn’t matter what amperage I feed the 80 breaker with. Does this make sense to anyone? I just want to make sure I am not missing anything.
I am a licensed electrician in Connecticut employed by a chemical plant. We were told to put in a temporary outlet for an electric truck to use for moving loads as a trial. We found a spare 150amp breaker and used this to feed a 480volt outlet. When we plug the charger in all is good. The charger has an 80 amp breaker in it, when we plug the truck into charge the 80 amp breaker trips. Our main breaker is ok. The company is saying we are feeding it with too high of an amperage and that’s the problem. To me this doesn’t make sense, the way I see it doesn’t matter what amperage I feed the 80 breaker with. Does this make sense to anyone? I just want to make sure I am not missing anything.