Electric vehicle charger with 50 amp plug
mlnk
NEC 625.13 says chargers need to be "permanently connected and fastened in place" if they are over 20 amp, 125 volts. But everybody is running 50 amp receptacles and using a 50 amp plug as the disconnecting means. Does permanently connected mean hard wired? And if not in sight of the circuit breaker or over 50 feet away you then need a disconnecting means like a pull out fuse box. So are all these thousands of installations not Code compliant?
Some AHJ's are encouraging their inspectors to use the 2017 as a guide to help resolve confusing language in previous code cycles.
NFPA-70 625.13 as it appears in 2011 was completely removed in the 2017 cycle, and may provide grounds for similar petitions of clarification.
I think you can even order those chargers with the cord pre-installed. What then, cut it off?
I have always had to use a range cord but I have had the jobs inspected and they passed.
The reason the united need to be fastened in place is obvious, they use the charger as a rack to store the cord when not in use.