R rose1981 Member Location TX Oct 23, 2015 #1 I have 10 electric vehicle charging station each one at 7200 kW. I wonder what demand factor to use. Can I use the same demand factor as receptacle?
I have 10 electric vehicle charging station each one at 7200 kW. I wonder what demand factor to use. Can I use the same demand factor as receptacle?
iwire Moderator Staff member Location Massachusetts Oct 24, 2015 #2 rose1981 said: I have 10 electric vehicle charging station each one at 7200 kW. I wonder what demand factor to use. Can I use the same demand factor as receptacle? Click to expand... What demand factor applies to receptacals?
rose1981 said: I have 10 electric vehicle charging station each one at 7200 kW. I wonder what demand factor to use. Can I use the same demand factor as receptacle? Click to expand... What demand factor applies to receptacals?
J JFletcher Senior Member Location Williamsburg, VA Oct 24, 2015 #3 rose1981 said: ... 7200 kW. Click to expand... Did you mean to type 7200W? 7200kW is 7.2 Megawatts. Anyway, here is a article by Mr Holt that may be of some help to you.
rose1981 said: ... 7200 kW. Click to expand... Did you mean to type 7200W? 7200kW is 7.2 Megawatts. Anyway, here is a article by Mr Holt that may be of some help to you.
Rampage_Rick Senior Member Location British Columbia, Canada Oct 24, 2015 #4 30A EVSEs mean 40A conductors and breakers. Pretty standard for anything other than Tesla. See this thread: http://forums.mikeholt.com/showthread.php?t=141171 Last edited: Oct 24, 2015
30A EVSEs mean 40A conductors and breakers. Pretty standard for anything other than Tesla. See this thread: http://forums.mikeholt.com/showthread.php?t=141171