Sparky2791
Senior Member
- Location
- Allentown, PA
I see that branch circuits are required to be designed to 125% for EV chargers because they are considered continuous load. I assume a service that is designed solely for EV chargers would also need to be sized for 125%. But how does one get to that conclusion via the NEC? 220.40 says.... Calculated load of a feeder or service shall not less than the sum of the branch circuits on the loads supplied, as determined by Part 2 of this article.
Example EV Charger Service has 530A of connected load. so... 600A service or 530A x1 25% = 662A (800A service)
Maybe I am making this more difficult than it has to be. Once you go down the rabbits hole......
Thanks for the replies!
Example EV Charger Service has 530A of connected load. so... 600A service or 530A x1 25% = 662A (800A service)
Maybe I am making this more difficult than it has to be. Once you go down the rabbits hole......
Thanks for the replies!