I see that branch circuits are required to be designed to 125% for EV chargers because they are considered continuous load. I assume a service that is designed solely for EV chargers would also need to be sized for 125%. But how does one get to that conclusion via the NEC? 220.40 says.... Calculated load of a feeder or service shall not less than the sum of the branch circuits on the loads supplied, as determined by Part 2 of this article.
Example EV Charger Service has 530A of connected load. so... 600A service or 530A x1 25% = 662A (800A service)
Maybe I am making this more difficult than it has to be. Once you go down the rabbits hole......
Thanks for the replies!