I need some help with OCP for individual welders. I have attached a specification sheet from the manual.
I had design to 90 amp CB. This was a project I did some time ago and now finally under construction. I been asked to review the submittals for the gear.
I have reviewed NEC 630 but still confused if something less than 90 amp breakers would be acceptable. The spec. say maximum effective supply current is 34.1. I am thinking I can use a 35-40amp breaker. It as list minimum conductor size #8awg. But, the maximum Time-delay fuse is 90 so the #8 wire is now not protected.
Thanks.
I had design to 90 amp CB. This was a project I did some time ago and now finally under construction. I been asked to review the submittals for the gear.
I have reviewed NEC 630 but still confused if something less than 90 amp breakers would be acceptable. The spec. say maximum effective supply current is 34.1. I am thinking I can use a 35-40amp breaker. It as list minimum conductor size #8awg. But, the maximum Time-delay fuse is 90 so the #8 wire is now not protected.
Thanks.