Electrical Area Classification for Hot Oil System

scrub12

Member
Location
Cleveland, OH
Occupation
Electrical Engineer
For hot oil systems, specifically, class IIIB liquids with high flash points, is electrical area classification typically required for valves, pumps, etc.? NFPA 497 4.2.7.3 states"A Class IIIB liquid will cool below its flash point very quickly when released. Therefore, area classification is SELDOM needed". When would it be needed, any advice here is greatly appreciated!
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I probably never would. However, if you are seriously concerned, compare the product's MSDS flash point and with the local high ambient.
 