Just wondering if the electrical box fill calculations, meant for outlet boxes, also apply to equipment cabinets too?
Cabinet.
An enclosure that is designed for either surface mounting or flush mounting and is provided with a frame, mat, or trim in which a swinging door or doors are or can be hung.
312.6(A) seems to say that a wiring duct shall be installed for wiring inside an electrical cabinet.
Do I understand that right? Meaning you can't just have loose or wiring routed within with just plastic ties.
As far as spacing requirements, it just says make sure there's adequate space.
However the most common "junction box" that I use is covered by Article 312. Junction boxes that have covers that "telescope" over the box are listed as "cutout boxes" and covered by Article 312 per the scope. Since the scope of 314 applies to all boxes used as junction boxes, both articles apply to "cutout boxes".Cabinets are covered by Art 312, Boxes by Art 314.
312.6-312.9 address conductors.