Forqnc
Member
- Location
- Elizabeth City, NC
- Occupation
- Electrical Controls Engineer
Hi, we had a customer recently tell us their company paid for NFPA to come on their site to confirm their classification zones.
They informed us that they where told if an electrical cabinet, with a Class 1 Div 2 rated HMI, is installed 6ft away from the opening of were flammable chemicals are added to their process and the cabinet is purged protected that area is a Class 1 Div 2 which makes the electrical cabinet ok to be there?
I've looked through section 5 but nothing jumps out at me about a 6ft spacing and classification change.
Any assistance is appreciated.
They informed us that they where told if an electrical cabinet, with a Class 1 Div 2 rated HMI, is installed 6ft away from the opening of were flammable chemicals are added to their process and the cabinet is purged protected that area is a Class 1 Div 2 which makes the electrical cabinet ok to be there?
I've looked through section 5 but nothing jumps out at me about a 6ft spacing and classification change.
Any assistance is appreciated.