For an apartment building with 3 services where the disconnect and metering equipment (for each of 3 services) is located on 2nd, 3rd, and 4th floors an electrical duct bank is needed to get the service entrance conductors to their respective main disconnect (so they'll be considered running outside of the building). This will be concrete enclosed duct bank (running vertically from ground up to each floor). Once I figure out all the conductor and conduit sizes. How do I determine the separation between the ducts? Is it just 2 inches between each one? And then 2 inches to the edge? For the conductors to be considered outside of the building? Or is there more to it than that? (ANNEX B?)
EX. Lets say that there are (3) 1200 amp services (1) on each of the 2nd, 3rd, 4th floors. Each 1200 amp service will require (4) sets of 500 kcmil (alu 75 degree) conductors each set in 4in conduit. Thats a total of 12 sets of conductors (4in conduits for all three services to the building). So by my calculations a 38" by 14" duct bank (with 2 columns and 6 rows of ducts) will be needed. Is this right?
EX. Lets say that there are (3) 1200 amp services (1) on each of the 2nd, 3rd, 4th floors. Each 1200 amp service will require (4) sets of 500 kcmil (alu 75 degree) conductors each set in 4in conduit. Thats a total of 12 sets of conductors (4in conduits for all three services to the building). So by my calculations a 38" by 14" duct bank (with 2 columns and 6 rows of ducts) will be needed. Is this right?