Electrical Enclosure Clearance

RNLENI

Member
Location
Michigan
Occupation
Engineer
Hi All,

I have an enclosure 120VAC mounted on a skid . There is 42 inch clearance at the front of the enclosure. But the skid frame is extending 5.8 inches from the front of the panel. But it at the floor (frame thickness will be around 6 inches from the ground level) .Is that oke? Or we can't have the skid frame extending in front?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
See 110.26(A)(3) in the 2020 or 2023 code. Six inches or less of a support structure in front of the face of the enclosure is not a code violation.
 