The only item required to be "readily accessible" from the air conditioning and refrigeration equipment is the disconnecting means. This is per article 440.
I am looking at a remote condensing unit that has the disconnecting means located at ground level, within sight of the refrigeration equipment and in compliance with the article 100 definition of "readily accessible".
However, the rest of the electrical enclosure is mounted with the equipment, which is around 10 feet in the air. Is this installation compliant?
To clarify, the equipment itself is not readily accessible. The disconnecting means is readily accessible. Is the disconnecting means the only thing required to be readily accessible?