Eff values are better now for new energy efficient motors, but if you don't know, 0.8 is a "safe" bet in that if you use it, you will end up estimating a bit high as opposed to a bit low. But large motors, i.e. above NEMA frames (roughly over 250HP), are typically 90-95% efficient, so I use 90% most of the time. The best thing is to get the efficiency values from the motor nameplates or from the suppliers if it isn't there.The first thing I noticed is that you are missing the term for the motor's efficiency, which is due to hysteresis losses in the core and windage of the spinning rotor. The estimate that I use for smaller motors is an efficiency of about 0.8, but this would likely increase with larger motors, and you might find it on the motor nameplate.
P = I * V * eff * pf * 1000 = KW
KWhr = KW * time
Cost = KWhr * rate($ / KWhr) = $
D'oh! I just got caught doing the same thing...Oops. I am so accustomed to using this when converting hp to current draw that I think I made a mistake by including the efficiency in this equation. I think that term comes in only when dealing with the shaft output power.
Another Edit: Also, if your amperage is per-phase, then don't forget the squareroot-3 term.
Energy efficiency has nothing to do with calculating the cost of electricity for an existing system.