Can we install Power cable in the same cable tray from ATS supplying the essential load and Incoming Norrmal Source to ATS?
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
When you say essential load, are you talking Healthcare and article 517? If so describe your situation in more detail, please.
 

sabbie

Member
Location
Jeddah
Occupation
Electrical Engineer
When you say essential load, are you talking Healthcare and article 517? If so describe your situation in more detail, please.
Dear Sir,

It is related to Pedestrian underpasses., Where the power cable for Emergency Source and Normal Source are combined in the same Cable tray? Kindly advise, it is acceptable by the code? if not, Which particular clause or articles it belongs?
 

ron

Senior Member
Dear Sir,

It is related to Pedestrian underpasses., Where the power cable for Emergency Source and Normal Source are combined in the same Cable tray? Kindly advise, it is acceptable by the code? if not, Which particular clause or articles it belongs?
What kind of load is this ATS serving? Is it an Article 700, 701, 702 or 517 load? Is the normal source an Article 230 utility service?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
It's probably permissible, but I would argue that this would be an unwise design decision. Any event that might cause damage to the primary supply cable is likely to affect the emergency feed as well. For my two cents, I'd like to see both horizontal and vertical separation of these cables, in the neighborhood of 5 - 10 feet, if feasible.
 