Project I am involved with is installing (5) combination Eye-Wash/Shower stations. They are electric, on-demand for tempered water and cut sheet states they are 126kW and 152A at 480V, 3-phase. They are all located in an area about 250' by 200', not all in straight line of each other (you'll understand why I present this area). Client requested putting these (5) units on a separate panel so we don't use up pole space off the main gear which I think is a good idea. Question is - what size panel do I need to go with and is there an exception is the code I can reference to avoid sizing the panel to the full demand if all (5) were running? The likelihood of having to use (5) of these at the same time is probably impossible, but I felt like if I sized the panel for worst case running (2) of these units, a 400Amp panel would suffice. Can I reference 220.60 as an exception to not sizing the panel for all (5) units running? Thougths?