Hi,
There have been some debate regarding the routing of bare copper conductor in with the steel underground water pipes (in contact with each each other).
The construction team wanted to do it to save time and cost in excavation works, while the design engineers doesn't want to because of the effects of galvanic reactions. Here's the recommendation from the design engineers:
To qoute:
"Routing the ground grid in parallel with the fire water line is not recommended due to the following reasons:
a) Galvanic reaction between dissimilar metals: Two different metals should never be routed in contact with each other. The metal which is less ?noble? (in this case the fire water pipe) will corrode easily. This is especially true during rainy season in the Philippines where the soil will be usually wet. The wet soil acts as an electrolyte for the fire water pipes and ground grid copper wires.
b) Ground grids will contain stray currents since they are expected to carry line-to-ground faults and, thus, hastening the effect of the galvanic reaction.
c) Fire water pipes are considered to be critical for safety and cannot be subjected to the effects of galvanic corrosion.
Please refer to the attached excerpt from paragraph 4.4.5 of IEEE 142 for the concept of galvanic reaction between two dissimilar type of metals. If routing of the fire water line and the ground grid cannot be avoided, a minimum spacing of 600mm (based on another project) should be maintained between them."
Any comment about this anyone?
There have been some debate regarding the routing of bare copper conductor in with the steel underground water pipes (in contact with each each other).
The construction team wanted to do it to save time and cost in excavation works, while the design engineers doesn't want to because of the effects of galvanic reactions. Here's the recommendation from the design engineers:
To qoute:
"Routing the ground grid in parallel with the fire water line is not recommended due to the following reasons:
a) Galvanic reaction between dissimilar metals: Two different metals should never be routed in contact with each other. The metal which is less ?noble? (in this case the fire water pipe) will corrode easily. This is especially true during rainy season in the Philippines where the soil will be usually wet. The wet soil acts as an electrolyte for the fire water pipes and ground grid copper wires.
b) Ground grids will contain stray currents since they are expected to carry line-to-ground faults and, thus, hastening the effect of the galvanic reaction.
c) Fire water pipes are considered to be critical for safety and cannot be subjected to the effects of galvanic corrosion.
Please refer to the attached excerpt from paragraph 4.4.5 of IEEE 142 for the concept of galvanic reaction between two dissimilar type of metals. If routing of the fire water line and the ground grid cannot be avoided, a minimum spacing of 600mm (based on another project) should be maintained between them."
Any comment about this anyone?