• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

ELECTRICAL GROUNDING SAFETY - Southern California Gas Company

Merry Christmas
Status
Not open for further replies.

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
I receive almost weekly these underground alerts brochures from many utilities. But this one caught my attention, since it specifically mentions Electrical Grounding.
 

Attachments

  • Electrical Grounding Safety #1.jpg
    Electrical Grounding Safety #1.jpg
    805.4 KB · Views: 11
  • Electrical Grounding Safety #2.jpg
    Electrical Grounding Safety #2.jpg
    1.2 MB · Views: 11
  • Electrical Grounding Safety #3.jpg
    Electrical Grounding Safety #3.jpg
    914.1 KB · Views: 11

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
It isn’t about electrical safety, per se. They simply don’t want a rod driven through their gas line.

I agree, but it brought back memories of when a crew was installing the new 170 controller cabinet, and at that time the county was installing a second ground rod, when it punched through a telephone main trunkline that took out the whole city for a couple of days. So, yes you really have to be careful where you drive a ground rod.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
There was an incident in SoCalGas territory a year or so ago where a solar installer put a rod through a gas pipe and someone died, iirc. Probably why they put that out.

IMO a good argument against AHJs enforcing the latest NEC grounding requirements on existing buildings. For solar or anything else, including resi overhead service upgrades. If the building has any grounding and you aren't doing digging and can't put in a ufer, let them go with the existing grounding. More lives were lost in that one incident than were saved by the hundreds of thousands of ground rods that have been required on residential solar installations in California.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
the county was installing a second ground rod, when it punched through a telephone main trunkline that took out the whole city
Good argument for calling Dig Alert for ground rods.
More lives were lost in that one incident than were saved by the hundreds of thousands of ground rods
Too many ignoramuses install ground rods, before calling 811.

Dig Alert is free, if called before possible damages.
 
Status
Not open for further replies.
Top