V VENgineer Member Location Miramar Fl Occupation Electrical Engineer Feb 22, 2024 #1 It seems illegal to me, in my opinion, but I can't find the article in the NEC that specifies it. Could you help me?
It seems illegal to me, in my opinion, but I can't find the article in the NEC that specifies it. Could you help me?
V VENgineer Member Location Miramar Fl Occupation Electrical Engineer Feb 22, 2024 #2 Plumbing conduit used like electrical conduit. Clearance violation.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Feb 22, 2024 #3 VENgineer said: It seems illegal to me, in my opinion, but I can't find the article in the NEC that specifies it. Could you help me?View attachment 2570213 Click to expand... 110.26(A) and the xxx.30 section of whatever wiring method that is.
VENgineer said: It seems illegal to me, in my opinion, but I can't find the article in the NEC that specifies it. Could you help me?View attachment 2570213 Click to expand... 110.26(A) and the xxx.30 section of whatever wiring method that is.
V VENgineer Member Location Miramar Fl Occupation Electrical Engineer Feb 23, 2024 #4 Does this OCPD comply with the 'Readily Accessible' requirement, or is it necessary to remove the receptacles?
Does this OCPD comply with the 'Readily Accessible' requirement, or is it necessary to remove the receptacles?