I've got a set of drawings issued by a subcontractor that calls for lighting load to be increased by 125%. He's referencing NEC 215.2(A)(1), however this is for feeders - not lighting - so I don't see where this is coming from.
Also for his total load calculation, he's adding another 20%. The largest motor load is correctly sized up to 125% of FLA per 430.24, but I don't see the justification for the 125% on lighting or the additional 20% applied to the overall load in volt-amps, which includes Receptacles, HVAC, Kitchen appliances and 'other loads'.
Am I missing something?
Thanks in advance.
I've got a set of drawings issued by a subcontractor that calls for lighting load to be increased by 125%. He's referencing NEC 215.2(A)(1), however this is for feeders - not lighting - so I don't see where this is coming from.
Also for his total load calculation, he's adding another 20%. The largest motor load is correctly sized up to 125% of FLA per 430.24, but I don't see the justification for the 125% on lighting or the additional 20% applied to the overall load in volt-amps, which includes Receptacles, HVAC, Kitchen appliances and 'other loads'.