They can be supplied from the fire system but if they are they need to be included in the battery calculations.
from NFPA 72 (National fire alarm code):
4.4.1.3 Power Supply Sources.
4.4.1.3.1 At least two independent and reliable power supplies shall be provided, one
primary and one secondary, each of which shall be of adequate capacity for the application.
4.4.1.3.2 Monitoring the integrity of power supplies shall be in accordance with 4.4.7.3.
4.4.1.4 Primary Power Supply.
4.4.1.4.1
Dedicated Branch Circuit. A dedicated branch circuit of one of the following
shall supply primary power:
(1) Commercial light and power
(2) An engine-driven generator or equivalent in accordance with 4.4.1.9.2, where a
person specifically trained in its operation is on duty at all times
(3) An engine-driven generator or equivalent arranged for cogeneration with
commercial light and power in accordance with 4.4.1.9.2, where a person
specifically trained in its operation is on duty at all times
question: if the branch circuit is
Dedicated Branch Circuit for Fire alarm system, how can supply electromagnet device from the same branch?