benjamin8761
Sr Electrical Engineer
- Location
- Laconia
- Occupation
- Electrical Engineer, PE
Existing Description:
We are modifying an apartment with a mix of cloth wiring and Romex with 1980's style SQ-D type QO load center. There are no Arc Fault breakers or GFCI protection. We are essentially looking at a early 1980's renovation which utilized existing conductors (Cloth). The receptacle spacing/requirements do not meet todays code.
Modifications:
The lighting will be replaced complete with switches - device (Greater than 6 feet of new wire 21012-D). This will require the installation of Arc Fault breakers.
This will more than likely require a panel upgrade because the new breakers will not fit into the ~45 year old panel. We will then need to supply Arc Fault breakers for the receptacles, if we have shared neutrals, we will have complete failure of these devices or nuisance trips. Now we need to replace the wiring of the receptacles.
The receptacles do not have the appropriate spacing, we will need to upgrade the spacing to meet code because we touched a receptacle.
Question
How far do we need to go per code and how far should we go?
We want to make improvements and not have the general improvements stopped because of creep.
This is an ongoing problem - How far do you go.
We are modifying an apartment with a mix of cloth wiring and Romex with 1980's style SQ-D type QO load center. There are no Arc Fault breakers or GFCI protection. We are essentially looking at a early 1980's renovation which utilized existing conductors (Cloth). The receptacle spacing/requirements do not meet todays code.
Modifications:
The lighting will be replaced complete with switches - device (Greater than 6 feet of new wire 21012-D). This will require the installation of Arc Fault breakers.
This will more than likely require a panel upgrade because the new breakers will not fit into the ~45 year old panel. We will then need to supply Arc Fault breakers for the receptacles, if we have shared neutrals, we will have complete failure of these devices or nuisance trips. Now we need to replace the wiring of the receptacles.
The receptacles do not have the appropriate spacing, we will need to upgrade the spacing to meet code because we touched a receptacle.
Question
How far do we need to go per code and how far should we go?
We want to make improvements and not have the general improvements stopped because of creep.
This is an ongoing problem - How far do you go.