Re: Electrical Outlet Height /Garage

Originally posted by bennie:
In this state, all receptacles are at 18 inches minimum. The cord cap, on the appliance, has been ruled a source of ignition if removed or installed under load.
So how does the code presume that all receptacles in a garage will have an appliance plugged into them?
 
Re: Electrical Outlet Height /Garage

I don't know that there is a specific height requirement but someone had suggested that I mount garage receptacles higher than 48" aff because if a homeowner were to store or lean a sheet of plywood or sheetrock against the wall it would clear the bottom of the receptacle. It made sense to me so I've been mounting them at about 54" aff ever since.
 
Re: Electrical Outlet Height /Garage

rcarrol: I owe you an apology as I was perusing the 99NEC handbook and happened on this very topic by accident. The handbook said that it did not consider the space behind freezers inaccessible. Guess they never met my relatives. single recept unless dedicated space with freezer in it, which would make it inaccessible.

paul
 
Re: Electrical Outlet Height /Garage

A local addendum here says a dedicated non gfi single receptacle will have a label appliance use only....How that stops MR. Homeowner from using it as a branch receptacle is beyond me.Also if you dun a dedicated circuit it has to be a single receptacle.
 
Re: Electrical Outlet Height /Garage

before some one jumps dead in my.... The appliance only is for garage receptacles only.Tom where do i find this in the NEC
 
Re: Electrical Outlet Height /Garage

Originally posted by ca_c10:
If you install an outlet less than 18" in a garage, regardless of residential or commercial, you will have to install EY(Explosion Proof)fittings. Read NEC 505-9(c) Class I Zone 2. The reasoning is that should you spill gasoline or other flammable liquids, the vapors will dissipate before reaching the 18" mark. Look at all GAS water heaters and you will see that they are all installed on 18" minimum platforms.
No.
 
Re: Electrical Outlet Height /Garage

though not directly stayted, would not 505.4 "Documentation for Industrial Occupancies" exculde residencal. we are not requierd to class and document our garages.
 
Re: Electrical Outlet Height /Garage

Residential garages are considered "Ordinary", that is, they are not classified.
If they were, we would never be allowed to have a freezer or refigerator in a garage!
I agree with this post above and the original poster!
 
Re: Electrical Outlet Height /Garage

Originally posted by websparky:
Residential garages are considered "Ordinary", that is, they are not classified.
If they were, we would never be allowed to have a freezer or refigerator in a garage!
I agree with this post above and the original poster!
Come on Dave, you have not seen the Class 1 Division 1 freezers at Sears. :D
 