Electrical outlets in pvc junction boxes

Status
Not open for further replies.

Mtech74

New User
Location
Florida
Occupation
Electrical Contractor
Question: Which section of the NEC covers the proper type of enclosure that can house an electrical outlet? Found a handy box installed inside of an 8x8x8 pvc junction box outside of the home. Not sure if this is acceptable.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Code doesn't work that way. Generally, it tells you what you can't do. Sometimes it reiterates what you can do (e.g. uses permitted). I've seen device boxes in larger outside enclosures many times. If there is a section that prohibits that, I don't know what it is. That receptacle probably needs to be GFCI protected though.
 

jap

Senior Member
Occupation
Electrician
Take the lid off the PVC box to access the receptacle and the PVC box has lost it's rating,,,, put the lid on to satisfy the rating of the PVC box and the receptacle becomes inaccessible,,, take the lid off to access the receptacle and the PVC box has lost it's rating,,, put the lid on and the receptacle becomes inaccessible,,,

Grab a chair and some popcorn,,, this is going to be comical,,, :)


JAP>
 

raberding

Senior Member
Location
Dayton, OH
Occupation
Consulting Engineer
Take the lid off the PVC box to access the receptacle and the PVC box has lost it's rating,,,, put the lid on to satisfy the rating of the PVC box and the receptacle becomes inaccessible,,, take the lid off to access the receptacle and the PVC box has lost it's rating,,, put the lid on and the receptacle becomes inaccessible,,,

Grab a chair and some popcorn,,, this is going to be comical,,, :)


JAP>
Schrodinger's receptacle.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Usually the purpose of these is to power a cord and plug item that resides in the box, or as a receptacle for temporary use when the j box lid is off.

We had giant roof boxes with many coax cables coming into them. When we would use various antennas for a test, the receptacle in the giant 3R box was used to power transmitters or spectrum analyzers. When the test was done, the cord and plug items were taken away and the 3R box was closed up. Yes, that receptacle could have been mounted outside the big box using its own device box and in use cover. But it didnt work as well and was less safe because the cords would have to go over the lip of the box to reach that outside receptacle.
 