That depends on the depths of the various panels. Did you understand my example of a violation from my earlier post?Thanks for the quick answer. however under 110.26 (2) the width of the working space shall be 30" wide regardless the panel width, is there going be a problem?
Yes..i understand your example. I saw Smart$ post but didn't see your post when I was replying to him.That depends on the depths of the various panels. Did you understand my example of a violation from my earlier post?
You didn't state any measurements... so can't tell from here.Thanks for the quick answer. however under 110.26 (2) the width of the working space shall be 30" wide regardless the panel width, is there going be a problem?
thanks againYou didn't state any measurements... so can't tell from here.
Usual remedy for panel depth issues Charlie mentioned is to space out the panel with lesser depth (most often done with strut).
thanks again
If it is close to the exact relationships shown in the picture, the new panel might be OK because all of the required clearance width could be to the right of the left edge of the panel and the transformer might not intrude into that space.Is that a panel above the transformer? If it's you have a problem with the depth. Because the transformer has a large profile.