zam
- New York, NY
How common is it to come across electrical panelboards in commercial settings that have more that 42 circuit breakers? Panels with 54 poles, 66 poles, 78 poles and 84 poles are manufactured by Siemens. Thank you.
Not very common at all, they haven't been around that long, besides who wants a panel you have to get down on your knees to land breakers in.
Assume you are referring to wire marker tags. I bet you can get another version with 46-90 tags, that is common with other brands anyway.Also, our Brady tags only go to 45![]()
We have yet to see an engineer spec a larger than 42 circuit panel. We will use two or three 42 circuits panels together on the same feeder instead of one larger panel.
The question becomes do they actually have an issue with more then 42 circuits in one panel or are they just doing it the way they have always done it and/or won't change their boiler plate?
Then you haven't been in my office lately. :lol: I have done it several times recently, including one current project. It happens when the architect doesn't give me much space for electrical equipment, and the owner has lots of toys that need power.We have yet to see an engineer spec a larger than 42 circuit panel.
You can start at floor level and stack them until you reach 6 feet 7 inches high with the highest handle. Since they eliminated the 42 circuit rule a couple codes ago they can now all be in the same cabinet on the same panelboard. I don't know of anyone making more then an 84 circuit panel though.Thank you all for replying back. This question arose because of a current project that we are working on where more than 42 circuit breakers are needed, but the wall has space (NEC clearance requirement) for only one electrical panel.