Article 409 covers control panels in the NEC (2011 shown) as below.
As far as I know you should be able to establish an SCCR for your panels if they don't have one. Basically it will be the same rating as the lowest rated component
in the panel. I recently compiled label data for about 20 panels where I work. These were built either by myself or other contractors and had no 'official' label or rating. As a plant safety project I had an Arc Flash study done and labels made for any panels that needed labels. There is a ton of info available on establishing SCCR ratings for panels on the net.
409.110 Marking. An industrial control panel shall be
marked with the following information that is plainly visible
after installation:
(1) Manufacturer’s name, trademark, or other descriptive
marking by which the organization responsible for the
product can be identified.
ARTICLE 409—INDUSTRIAL CONTROL PANELS 409.110
2011
(2) Supply voltage, number of phases, frequency, and fullload
current for each incoming supply circuit.
(3) Industrial control panels supplied by more than one
power source such that more than one disconnecting
means is required to disconnect all power within the
control panel shall be marked to indicate that more than
one disconnecting means is required to de-energize the
equipment.
(4) Short-circuit current rating of the industrial control
panel based on one of the following:
a. Short-circuit current rating of a listed and labeled
assembly
b. Short-circuit current rating established utilizing an
approved method
Informational Note: UL 508A-2001, Standard for Industrial
Control Panels, Supplement SB, is an example of an
approved method.
Exception to (4): Short-circuit current rating markings are
not required for industrial control panels containing only
control circuit components.
(5) If the industrial control panel is intended as service
equipment, it shall be marked to identify it as being
suitable for use as service equipment.
(6) Electrical wiring diagram or the identification number
of a separate electrical wiring diagram or a designation
referenced in a separate wiring diagram.
(7) An enclosure type number shall be marked on the industrial
control panel enclosure.