Steve Ragan
- Austin, Texas
I have an electrical engineer stating that it is OK to put a 2 pole 40amp Cutler Hammer breaker in a GE panel, I did not know that you could mix breakers in panels.
The breaker would have to be listed for use in the panel. Some Cutler Hammer breakers are classified for use in other panels, you'd have to check the specific breaker manufacturer information to be sure.
If the Cutler Hammer breakers fits in a GE panel it is either the BR series or hopefully one that is listed for GE. Almost all the manufacturers have made breakers listed for the competitions panels.
That is correct. The only breakers that are listed for use in a panel are those that were manufactured by the company that made the panel. The other breakers that UL says you can use are "classified" for that use. This is a case where UL is saying that 110.3(B) does not apply:?I was under the assumption that the breakers were not listed they were "classified" for specific models of competing panels.
What this says to me is that 110.3(B) only applies to the instructions that are in the white book or the actual listing documents, not to the recommendations that are provided with the product by the manufacturer.I think it falls under the "yeah, yeah, whatever" clause in the back of the White Book. Nobody's perfect.![]()