Electrical pedestal

Status
Not open for further replies.
Main breaker


Sent from my iPhone using Tapatalk

I am assuming this is a service disconnect.

You will need a GES, grounding electrode system. Two rods and a #6 CU GEC will work.

You will need a 4 wire feed to whatever structure this pedestal serves.

That structure will need a GES and a disconnecting means.

Do not rebound neutral at structure.
 
Yes this is a service disconnect and it has a four wire feeding other structure. What article governs a pedestal?


Sent from my iPhone using Tapatalk
 
Under the 2017 NEC, if the pedestal is a self-contained manufactured electrical product installed in the ground, doesn't the revision to the definition of structure mean that the pedestal would not require a GES?

Cheers, Wayne
 
Under the 2017 NEC, if the pedestal is a self-contained manufactured electrical product installed in the ground, doesn't the revision to the definition of structure mean that the pedestal would not require a GES?

Cheers, Wayne

Again, it would depend what equipment that unit is comprised of.

Are these pedestals service equipment, receptacles, or what?

If you have a 2017, post the definition if you can.
 
Again, it would depend what equipment that unit is comprised of.

Are these pedestals service equipment, receptacles, or what?

If you have a 2017, post the definition if you can.
Fully agree. If pedestal would only have receptacle(s) in it - then worst case it is a structure supplied by a branch circuit. Supply it with a service or a feeder and it should need a grounding electrode system - typically ground rod(s) is what it used.

There is no NEC section that specifically is for pedestals.
 
If you have a 2017, post the definition if you can.
I don't have a 2017, but you can read it for free on nfpa.org. Of course they make it hard to copy text, it is a graphical view. But the new definition of Structure is short and easy to transcribe:

Structure. That which is built or constructed, other than equipment.

The definition of equipment appears unchanged from 2014.

Cheers, Wayne
 
I am assuming this is a service disconnect.

You will need a GES, grounding electrode system. Two rods and a #6 CU GEC will work.

You will need a 4 wire feed to whatever structure this pedestal serves.

That structure will need a GES and a disconnecting means.

Do not rebound neutral at structure.

Rebound?
Does that mean the rod could "rebound" back up out of the ground?:p
 