Electrical question

Trep21

Member
Location
New york
Occupation
Electrician
In a multi-unit dwellin of four stories, romex has been used for branch circuit wiring, SE cable encased in RMC was used for the service and emt runs through return air plenums extends outside to feed outside lights. According to NYC which of the following is true?

a. EMT not allowed in plenum ceilings
b. NM allowed in residence over three stories
c. SE in RMC
d. Emt allowed outside when treated against
corrosion with an approved means.
 

Perri Redder

Member
Location
NY
Occupation
Electrical Engineer/Electrician
I know C is true, A and B are false. D, hrm. I think it was true but hasn't been for a bit. I think people still do it even.
Final answer, C only. No google.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
C.
Because:
EMT is permitted in plenum ceilings
NM cable is not permitted in multi-unit dwellings above 3 stories
EMT is not permitted in wet locations
 