the 2020 NEC section550.15 (H) (1) requires under chassis wiring exposed to weather to be protected by a conduit or raceway identified for use in wet locations.
(2) indicates where wiring is exposed to physical damage it shall be protected by a raceway, conduit or other means.
Table 300.5 indicates in column 3 location of wiring method or Circuit indicates that under a building which a mobile home is a building that the burial depth is 0.
The question is can the conduit for the feeder to the main panel for the home lay on the ground?