electrical room door (6 ft?)

Status
Not open for further replies.

dannyrzk

Member
Location
tulsa, OK
Good morning, WE have a service switch of 2000amp, which will require compliance with NMEC 110.26. Here is my question, if I don't have the space to swing two door (36"), can I have just one 6 ft. door in the room?

I thought I read before, but I may be wrong.

Thanks
 
It may depend on which code cycle you are under, and whether the equipment is wider than 6 feet. But the basic rule is that you need an egress path on both sides of the working space. Putting a wider door does not create a second egress path. Is it possible for you to take advantage of one of the two exceptions to that rule (i.e., unobstructed path or double working space)?
 
It may depend on which code cycle you are under, and whether the equipment is wider than 6 feet. But the basic rule is that you need an egress path on both sides of the working space. Putting a wider door does not create a second egress path. Is it possible for you to take advantage of one of the two exceptions to that rule (i.e., unobstructed path or double working space)?

I see, I was wrong I then.

Appreciate you!
 