shortcircuit1
Senior Member
- Location
- USA
Bear with me on this. I was studying IBC Sec 1008.1.10(2012) about the Panic and Fire exit hardware. It mentions that
"Electrical rooms with equipment rated 1,200 amperes ormore and over 6 feet (1829 mm) wide that contain overcurrent
devices, switching devices or control devices with exit or
exit access doors shall be equipped with panic hardware or
fire exit hardware. The doors shall swing in the direction of
egress travel."
But if you go to NEC 2012 110.26 C(3) it mentions that
"Where equipment rated 1200 A or
more that contains overcurrent devices, switching devices,
or control devices is installed and there is a personnel
door(s) intended for entrance to and egress from the working
space less than 7.6 m (25 ft) from the nearest edge of the
working space, the door(s) shall open in the direction of
egress and be equipped with panic bars, pressure plates, or
other devices that are normally latched but open under simple
pressure."
My question is two parts:
1. In IBC it says if you have any equipment rated over 1200A and over 6ft wide then you need a exit door with panic hardware. But my question is not necessariliy every equipment that is over 6ft is rated over 1200A.For example you have meter banks which go over 6' with 5 stacks. In that case do you need to have egress door with panic hardware even though its not rated 1200A or more?
2. NEC and IBC conflict in terms of when you need panic hardware. NEC says its only when you have equipment rated over 1200A but IBC is both 1200A and 6ft wide. Which one should i take into consideration?
"Electrical rooms with equipment rated 1,200 amperes ormore and over 6 feet (1829 mm) wide that contain overcurrent
devices, switching devices or control devices with exit or
exit access doors shall be equipped with panic hardware or
fire exit hardware. The doors shall swing in the direction of
egress travel."
But if you go to NEC 2012 110.26 C(3) it mentions that
"Where equipment rated 1200 A or
more that contains overcurrent devices, switching devices,
or control devices is installed and there is a personnel
door(s) intended for entrance to and egress from the working
space less than 7.6 m (25 ft) from the nearest edge of the
working space, the door(s) shall open in the direction of
egress and be equipped with panic bars, pressure plates, or
other devices that are normally latched but open under simple
pressure."
My question is two parts:
1. In IBC it says if you have any equipment rated over 1200A and over 6ft wide then you need a exit door with panic hardware. But my question is not necessariliy every equipment that is over 6ft is rated over 1200A.For example you have meter banks which go over 6' with 5 stacks. In that case do you need to have egress door with panic hardware even though its not rated 1200A or more?
2. NEC and IBC conflict in terms of when you need panic hardware. NEC says its only when you have equipment rated over 1200A but IBC is both 1200A and 6ft wide. Which one should i take into consideration?