Hypothetically if you have two adjacent rooms both containing an 800A piece of electrical gear and there is a door between the two spaces. Would you be required to have a door with double sided panic hardware or remove the door completely?
 

WA_Sparky

Electrical Engineer
Location
Vancouver, WA, Clark
Occupation
Electrical Engineer
Oh no I envisioned this being two rooms. Hallway has a door that leads to room 1 (mech room). Inside mech room is another door to room 2 (existing electrical room). Renovation comes and no room for additional 800A so one is added to mech space. No egress door for electrical room would swing into Mech room. Egress door of mech room swings into hallway.

I'm guessing you just partially answered my original question. Door swing must open in direction of egress. So technically there shouldn't be any scenario where two rooms would have doors opening into eachother because path of egress will be one way?
 

BillyMac59

Senior Member
Location
Wasaga Beach, Ontario
Occupation
Industrial Electrician
By putting electrical switchgear in the mechanical room, you have made that room an electrical room. The rules for an electrical room now apply to the entire room. What about another wall between the newer switch gear and the rest of the mechanical room?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Oh no I envisioned this being two rooms. Hallway has a door that leads to room 1 (mech room). Inside mech room is another door to room 2 (existing electrical room). Renovation comes and no room for additional 800A so one is added to mech space. No egress door for electrical room would swing into Mech room. Egress door of mech room swings into hallway.

I'm guessing you just partially answered my original question. Door swing must open in direction of egress. So technically there shouldn't be any scenario where two rooms would have doors opening into eachother because path of egress will be one way?
One potential situation I can think of where you might have a bidirectional egress is where two exits from a room are required, and an exit to another room rather than to the outside will still qualify as an exit from the first work area even though the second room itself may also require an egress.
 

WA_Sparky

Electrical Engineer
Location
Vancouver, WA, Clark
Occupation
Electrical Engineer
One potential situation I can think of where you might have a bidirectional egress is where two exits from a room are required, and an exit to another room rather than to the outside will still qualify as an exit from the first work area even though the second room itself may also require an egress.
Perfect, so in this situation you mentioned above, would you tell architects to remove door between the two Electrical rooms (which id imagine makes two spaces one, therefore, each of the rooms remaining egress exits counts as (2) exits for the combined space)? Or is there a such thing as a door with panic hardware on both sides?
 