Electrical room Ground bus

Status
Not open for further replies.

sharan

Senior Member
Continuous Ground bus in electrical room - can this be mounted at any height? There are obstructions upto 5' AFF.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We mount them low or high sometimes even near the ceiling. The NEC is silent on this issue except to say that connections of the GEC must be accessible. {250.68(A)}
 