S sharan Senior Member Oct 3, 2017 #1 Continuous Ground bus in electrical room - can this be mounted at any height? There are obstructions upto 5' AFF.
Continuous Ground bus in electrical room - can this be mounted at any height? There are obstructions upto 5' AFF.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Oct 3, 2017 #2 We mount them low or high sometimes even near the ceiling. The NEC is silent on this issue except to say that connections of the GEC must be accessible. {250.68(A)}
We mount them low or high sometimes even near the ceiling. The NEC is silent on this issue except to say that connections of the GEC must be accessible. {250.68(A)}