The second question is if i put some switch on the left. I should maintain at least 8' work space, right?
Help me...
yesI would add that the 1200 amp switchboard also needs to be larger than 6' in width for that section to apply.
You mentioned 1200 amps, but I don't see that you have gear that fits into 110.26(C)(2) large equipment either, if you are concerned about entrance/egress from working space.
If you had a single 1200 amp switchboard this section would apply, you have multiple pieces of equipment but all are under 1200 amps.
you are right, so the code only apply to single equipment over 1200amp? Do we still need to concern about the Con-Edison end box which is 1200 amp.
only if that panel is more then 12" deep or if conditions would happen to require more then 3 feet of working space.Based on the drawing there is inadequate working space in front of the 200 amp disconnect for PP-CH