How so?Originally posted by marinesgt0411:
it may not be a NEC code violation but is often a local fire code violation I suggest you check with the local fire marshall
Originally posted by iwire:
ElectriycalrOOM = Electrical Equipment Room..?There is really no such thing as an 'electric room' as far as the code is concerned
What is the definition of an electric room?
* In Electrical Equipment Rooms,the illumination shall not be controlled by automatic means only..
iwire, this is one of those rooms , where,we can't control Illumination of lighting by automatic means alone..
surely you have seen one.. ..
Yes they sure do and they can be found in 110.26, none of which requires a dedicated room or prohibits storing 'stuff' in a room with electric equipment.Originally posted by wpaul29:
I cant site the actual material but the NFPA does have requirements for dedicated spaces that are used for electrical equipment.
Maybe by your insurance carrier or company policy but not by the NEC. We are not allowed to install a panel in a clothes closet.Originally posted by wpaul29:
Storing office supplies an or other things that might be easily egnitable is prohibited. In a more general sense the areas dedicated for electrical equipment are not storage rooms an shouldn't be used as such even though often you see you see it done.
Originally posted by wpaul29:
Im not talking about small residential or commercial work. Im talking about switchgear rooms transformer vaults an such. Installations with stepdown transformers distribution panels etc.
If you have a standard in mind let us know about it.Originally posted by wpaul29:
Also the NEC is a publication of the NFPA an they have othrer material that relates to what I was saying was prohibited.
That's understandable.Originally posted by sceepe:
However, on the flip side, I work in a local jurisdiction that says if the room has a transformer over 112 KVA, its an "electrical room" and they want it rated.
I do not see how this would effect storage in this room of rated construction.450.21 Dry-Type Transformers Installed Indoors.
450.21(B) Over 112 1/2 kVA. Individual dry-type transformers of more than 112 1/2 kVA rating shall be installed in a transformer room of fire-resistant construction. Unless specified otherwise in this article, the term fire resistant means a construction having a minimum fire rating of 1 hour.
Exception No. 1: Transformers with Class 155 or higher insulation systems and separated from combustible material by a fire-resistant, heat-insulating barrier or by not less than 1.83 m (6 ft) horizontally and 3.7 m (12 ft) vertically.
Exception No. 2: Transformers with Class 155 or higher insulation systems and completely enclosed except for ventilating openings.