An overhead residential 200 amp service was fed with 2/0 copper MTW between the meter and the electrical panel. As far as I know you need to feed a 200 amp main breaker with 3/0 copper, not 2/0. Is there an exception I may not be aware of in Connecticut?

Thanks, Tom
 
310.15(B)(7) is what you are looking for.
(7) Single-Phase Dwelling Services and Feeders. For onefamily
dwellings and the individual dwelling units of two-family
and multifamily dwellings, service and feeder conductors
supplied by a single-phase, 120/240-volt system shall be permitted
to be sized in accordance with 310.15(B)(7)(1) through
(4).
For one-family dwellings and the individual dwelling units of
two-family and multifamily dwellings, single-phase feeder
conductors consisting of 2 ungrounded conductors and the
neutral conductor from a 208Y/120 volt system shall be permitted
to be sized in accordance with 310.15(B)(7)(1) through
(3).
(1) For a service rated 100 through 400 amperes, the service
conductors supplying the entire load associated with a
one-family dwelling, or the service conductors supplying
the entire load associated with an individual dwelling unit
in a two-family or multifamily dwelling, shall be permitted
to have an ampacity not less than 83 percent of the service
rating.
(2) For a feeder rated 100 through 400 amperes, the feeder
conductors supplying the entire load associated with a
one-family dwelling, or the feeder conductors supplying
the entire load associated with an individual dwelling unit
in a two-family or multifamily dwelling, shall be permitted
to have an ampacity not less than 83 percent of the feeder
rating.
(3) In no case shall a feeder for an individual dwelling unit
be required to have an ampacity greater than that specified
in 310.15(B)(7)(1) or (2).
(4) Grounded conductors shall be permitted to be sized
smaller than the ungrounded conductors, if the requirements
of 220.61 and 230.42 for service conductors or the
requirements of 215.2 and 220.61 for feeder conductors
are met.

200A x 83% =166A
The 2/0 is allowed.
 
Pure MTW would be odd, but lots of stranded THHN is also rated MTW, and if the printing on the wire is hard to read or scraped off then one might only see the MTW designation.

-Jon
 
From Allied. As Jon said, some MTW also shows THHN / THWN-2:
MTW vs THHN Specs for Construction
MTW WireTHHN Wire
Conductor Size22 AWG-1000 MCM14 AWG-1000 MCM
Conductor TypeStrandedSolid or Stranded
Conductor MaterialBare or Tinned CopperBare Copper or Aluminum
Insulation MaterialPolyvinylchloride (PVC)Polyvinylchloride (PVC) with Nylon Jacket
Max. Temperature90°C90°C