Electrical service

Status
Not open for further replies.

Apaps03

Member
Location
Fair Lawn NJ
So this is my first time doing this and I need to know if im correct. I have a 4 apt dwelling that is 3000 sq ft. I did the following calculation to find the size of my service
Lighting 3000sq x 3 va= 9000va Small appliance 4 per apartment (2 counter @3000va ) (2 fridges @ 3000va) = 24000va Laundry 4 @1500 va = 6000Va (LAUNDRY IS GAS) I got 39000Va -3000 x.35 +3000 =15,600 for Lighting and Outlets
My other loads are 4 microwaves @1500va=6000
4 dishwashers@ 1500 =6000
4 range hoods @1500 =6000 Total Va 24000 @75% = 18000
4 air handlers @1500 =6000

Lastly I have 4 Rooftop Air condensors that say are 17 Amps at 240V. So i figured about 4500VA @100% = 18000VA

So if i add up my numbers 15,600+18,000+18,000=51,600Va divided by 240 equal 215 AMPs. DO I NEED TO APPLY 125%. So my service actually needs to be 262 AMPS?

So if that is correct and i use a 250 Amp service i should be fine right? Now if i do the same calculation per Apartment i get like 53.5 AMPs. DO I NEED TO APPLY THE 125% rule to So i would need to have 70 amp subpanels?


Any answers would help. Im so close to getting this job. Im sure the town is gonna beat me up on this too.
 
So this is my first time doing this and I need to know if im correct. I have a 4 apt dwelling that is 3000 sq ft. I did the following calculation to find the size of my service
Lighting 3000sq x 3 va= 9000va Small appliance 4 per apartment (2 counter @3000va ) (2 fridges @ 3000va) = 24000va Laundry 4 @1500 va = 6000Va (LAUNDRY IS GAS) I got 39000Va -3000 x.35 +3000 =15,600 for Lighting and Outlets
My other loads are 4 microwaves @1500va=6000
4 dishwashers@ 1500 =6000
4 range hoods @1500 =6000 Total Va 24000 @75% = 18000
4 air handlers @1500 =6000

Lastly I have 4 Rooftop Air condensors that say are 17 Amps at 240V. So i figured about 4500VA @100% = 18000VA

So if i add up my numbers 15,600+18,000+18,000=51,600Va divided by 240 equal 215 AMPs. DO I NEED TO APPLY 125%. So my service actually needs to be 262 AMPS?

So if that is correct and i use a 250 Amp service i should be fine right? Now if i do the same calculation per Apartment i get like 53.5 AMPs. DO I NEED TO APPLY THE 125% rule to So i would need to have 70 amp subpanels?


Any answers would help. Im so close to getting this job. Im sure the town is gonna beat me up on this too.

I would suggest you study the examples in the Informative Annex D. This can be a great help in learning how to do these calcs.
 
I did not check any of the work however you do not need to add 125% to the calculation.



Thanks Dennis, a follow up question would be does you general lighting load sq ft times va plus laundry and small appliance, 100% . 35% count towards your kitchen refrigerator, dishwasher, microwave. Is the 3va per square foot covering these items?
 