These required separations are taken from the NFPA National Fuel Gas Code Section 5.7.2.3 and NFPA Liquefied Petroleum Gas Code Table 3.2.2.2 (d): (1) Gas meters shall be located at least 3 ft. (0.9 m) from sources of ignition. (2) LP-Gas or propane cylinders that are exchanged (not filled on site), 5 ft. separation from external sources of ignition; PPL EU requires 6 ft. (3) For larger cylinders filled on site, 10 ft. separation from a source of ignition.
This is for commercial work we do.
Residential is kind of a mix between what the county requires and the propane company.
that being said our county inspector has never checked the distance once when weve installed generators and had new tanks put in.
But the propane company will send one of there guys out and inspect the location of where the tanks going to be installed and they require 15ft from an ignition source and 25 feet from any type of motor electrical or fuel powered.