We need to replace the Zinsco sub panels in some apartments in a 1960 building. The panels are in hall closets. Is the building grandfathered in codes to allow panels to remain in hall closet?
The NEC states the following: (D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.
plus, any location would require proper working clearance.
Any variations from those requirements such as grandfathering would be a local jurisdiction issue and not addressed by the NEC
The only recourse you have is to check with the local inspection department. Some places will allow replacements if the install was compliant at the time of the original install