The NESC is a performance code, in other words, the end result is the performance of the system. If a table requires 15 feet of clearance, then that 15 feet is under the worst of conditions. Here it is normally with 1/2 inch of ice at 32 degrees Fahrenheit and no wind. In other locations it may be heavy loaded wire on a hot day and no wind. With the short spans that electrical contractors use, 16 feet will do nicely under a prescriptive Code. The bottom line is about the same.
As far as enforcement of the NESC is concerned, it depends on the state and local areas as to who, if anybody, enforces the NESC. Generally speaking, it is the courts that enforce the NESC. In other words, someone has to be hurt (
or killed) or something has to be damaged (
or destroyed) and the case taken to court. If the electric utility has to pay too much in damages, they will start to comply with the NESC.
Speaking of service drops and service laterals, the requirements are in the NEC because there are situations where the customer is required to install the service drop or service lateral. Take the instance where the meter is installed at the property line without a disconnecting means. The customer would then be required to run the service conductors overhead or underground to his building. Remember, the meter is just the cash register, not service equipment.