With all of these restrictions, why would you install aluminum wiring for residential wiring. You have hundreds of connections to make that will expose you to a possible loose connection problem.
 

Attachments

  • Electrical Wiring - Residential - Aluminum_Page_1.jpg
    Electrical Wiring - Residential - Aluminum_Page_1.jpg
    168.5 KB · Views: 16
  • Electrical Wiring - Residential - Aluminum_Page_2.jpg
    Electrical Wiring - Residential - Aluminum_Page_2.jpg
    449.4 KB · Views: 14
  • Electrical Wiring - Residential - Aluminum_Page_3.jpg
    Electrical Wiring - Residential - Aluminum_Page_3.jpg
    478.4 KB · Views: 16
  • Electrical Wiring - Residential - Aluminum_Page_4.jpg
    Electrical Wiring - Residential - Aluminum_Page_4.jpg
    380.3 KB · Views: 13

kwired

Electron manager
Location
NE Nebraska
Aluminum conductors is not a problem for service and feeder conductors as a general rule - assuming you have terminals that accept aluminum conductors and same for maybe a 40 or 50 amp branch circuit.

Most common problems was back in 1960s and 1970's where solid 10 and 12 AWG conductors were used mostly in NM sheathed cable. I don't think you can even purchase this product new anymore nor have you been able to for 30+ years. So most the problems we have are dealing with existing installations that used it.
 

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
Is the torque value on terminals same as copper conductor?
I have not seen a designation on lets say meter mains, lugs take either copper or aluminum and they have a set torque value. Torque value from other post on here is not really accurate, its just a group of people agreed on those number . To many variables to have a proper number.
 

mikeames

Senior Member
Location
Germantown MD
Occupation
Teacher - Master Electrician - 2017 NEC
That's why the Alloy is specified (Since 1983). This alloy does not require anti-ox or whatever you want to call the compound.