Dear Sir,
We have a (difficult to access) underground room where we are planning to install a small ventilation fan (single phase,200 watts).The present electrical load in this room is a three phase pump with its remote starter(DOL) of capacity 3 h.p. three phase.
Now for the new load since it is difficult to lay a new cable(making a peneteration on the concrete wall,waterproofing,right of way, etc..) ,can we wire it on the pump incoming cable??.The scheme will be as follows:
The incoming cable will be routed thro a distribution board having
1. Incoming Isolator where the 3 phase cable from the remote DOL starter will be terminated.
2. After the Isolator the supply scheme will fork into two parts.One part(3 phase) going to a Motor protection breaker(this will provide o/c and s/c protection to the motor),as I will be cancelling the thermal overload in the remote DOL starter.The second part will go to a transformer with 415 volt primary and 230 volt secondary,which will then feed single phase to the ventilation fan in question.
Ofcourse I will be providing dp rccb for fan and fp rccb for pump in the distribution board for earth fault protection.
Is this scheme OK.What will be spec for transformer ,300 va single phase 415 volt (primary) and 230 volt(secondary)- is this ok??
One problem which I can visualise is that the fan will be ON only when pump is running , but I can live with it.!!
We have a (difficult to access) underground room where we are planning to install a small ventilation fan (single phase,200 watts).The present electrical load in this room is a three phase pump with its remote starter(DOL) of capacity 3 h.p. three phase.
Now for the new load since it is difficult to lay a new cable(making a peneteration on the concrete wall,waterproofing,right of way, etc..) ,can we wire it on the pump incoming cable??.The scheme will be as follows:
The incoming cable will be routed thro a distribution board having
1. Incoming Isolator where the 3 phase cable from the remote DOL starter will be terminated.
2. After the Isolator the supply scheme will fork into two parts.One part(3 phase) going to a Motor protection breaker(this will provide o/c and s/c protection to the motor),as I will be cancelling the thermal overload in the remote DOL starter.The second part will go to a transformer with 415 volt primary and 230 volt secondary,which will then feed single phase to the ventilation fan in question.
Ofcourse I will be providing dp rccb for fan and fp rccb for pump in the distribution board for earth fault protection.
Is this scheme OK.What will be spec for transformer ,300 va single phase 415 volt (primary) and 230 volt(secondary)- is this ok??
One problem which I can visualise is that the fan will be ON only when pump is running , but I can live with it.!!