A low voltage digital addressable lighting company makes the claim in their brochure that their control circuit may be run in the same cable or raceway as the lighting circuit. They also claim that the circuit may be run as class 1 or class two. They use Article 300.3 to back that up and say as long as the insulation of the control circuit is equal or greater than that of the lighting circuit then it is ok. However the FPN of 300.3 refers to 725 for specifics on class 2 and class 3 circuits. There it clearly states that a class two circuit shall be separated unless meeting some of the exceptions in which would not be done if wired the way recommend. The control circuit is a class 2 circuit. Does simply changing the insulation make that a class 1 or are classes determined by the power supply and thus making their claim a violation?