I am hooking up a bonded 17.5 kw portable generator ( generac ) to a new subpanel using a 50 amp inlet and a double pole double throw switch as the manual transfer switch . Since the generator is the bonded type this would be considered a separately derived system and the neutral would have to be switched as there can only be 1 bond point between the grounded conductor and the ground . Would a ground rod be required at the site of the inlet to be connected during use and can you see any code issues with this installation ? I will be using a 3 pole switch 2 phases and the neutral switched together,
 
I there any reason why you want this setup as an SDS? You could eliminate the MTS and grounding electrodes if you use the generator with an unbonded neutral.
 
I am hooking up a bonded 17.5 kw portable generator ( generac ) to a new subpanel using a 50 amp inlet and a double pole double throw switch as the manual transfer switch . Since the generator is the bonded type this would be considered a separately derived system and the neutral would have to be switched as there can only be 1 bond point between the grounded conductor and the ground . Would a ground rod be required at the site of the inlet to be connected during use and can you see any code issues with this installation ? I will be using a 3 pole switch 2 phases and the neutral switched together,

If you connect it this way and the existing N-G bond is outside the transfer switch, then yes. I think I would separate N and G at the generator, though, and not switch the N.
 
What is the model number of the generator?

I'm pretty certain the last 2 Generac 17.5kw portables we wired for, did not have a neutral bond connection (They floated)
 
I there any reason why you want this setup as an SDS? You could eliminate the MTS and grounding electrodes if you use the generator with an unbonded neutral.
I ordered a 2 pole switch and am now returning it for 3 pole as I did not supply generator . That being said do you see a problem with the install? I read online that for arcfault and gfi breakers this might be the preferrd method.
 