shaun m rice
Member
- Location
- hackensack n.j. usa
I am hooking up a bonded 17.5 kw portable generator ( generac ) to a new subpanel using a 50 amp inlet and a double pole double throw switch as the manual transfer switch . Since the generator is the bonded type this would be considered a separately derived system and the neutral would have to be switched as there can only be 1 bond point between the grounded conductor and the ground . Would a ground rod be required at the site of the inlet to be connected during use and can you see any code issues with this installation ? I will be using a 3 pole switch 2 phases and the neutral switched together,