The sizing requirements for the main bonding and system bonding jumpers are covered in 250.28(D). Where there are parallel sets of service or supply conductors and the total circular mil area for the largest individual phase set exceeds 1100 kcmil copper or 1750 kcmil aluminum (the point at which Table 250.66 reaches it maximum size), the MBJ or SBJ is sized based on 12.5% of the largest parallel set. This section also covers the method for sizing the MBJ or SBJ where the bonding jumper conductor material differs from that of the circuit conductors. The following is an example of sizing a copper main or system bonding jumper where the ungrounded conductors are installed in parallel:
4 sets of parallel 500 kcmil (500,000 cmil) copper supply conductors.
All parallel sets (A, B, & C phases) are the same size.
Largest individual phase set: 4 x 500,000 = 2,000,000 cmil.
MBJ or SBJ size: 2,000,000 x .125 (12.5%) = 250,000 cmil
MBJ or SBJ = 250 kcmil copper
Another example using aluminum ungrounded conductors were aluminum and a copper bonding jumper.
2 sets of parallel 750 kcmil (750,000 cmil) aluminum supply conductors
All parallel sets (A, B, & C phases) are the same size.
Largest individual phase set: 3 x 750,000 = 2,250,000 cmil.
MBJ or SBJ size: