kstall said:if you pull a ground wire in to emt .
jwelectric said:I would say that the EMT was the EGC that would bond the box and the installation you are describing would be compliant unless you are wanting to have an isolated ground in which case the device would need to be of the type that would allow this.
iwire said:jwelectric said:I would say that the EMT was the EGC that would bond the box and the installation you are describing would be compliant unless you are wanting to have an isolated ground in which case the device would need to be of the type that would allow this.
iwire said:Mike regardless of it being EMT, if you pull a EGC you must bond it to box unless there are no splices.
But you know that so whats up?
M. D. said:perhaps Mike is thinking 250.146(d)