Can flexible cord be used under a computer floor? I have a 200 amp printer to feed. 208 3phase. Type SC cable.
Thanks, Sparky 56
 
Last edited:
See 645.5(D)(2)

(2) The branch-circuit supply conductors to receptacles or field-wired equipment are in rigid metal conduit, rigid nonmetallic conduit, intermediate metal conduit, electrical metallic tubing, electrical nonmetallic tubing, metal wireway, nonmetallic wireway, surface metal raceway with metal cover, nonmetallic surface raceway, flexible metal conduit, liquidtight flexible metal conduit, or liquidtight flexible nonmetallic conduit, Type MI cable, Type MC cable, or Type AC cable. These supply conductors shall be installed in accordance with the requirements of 300.11.
 
sparky56 said:
Can flexible cord be used under a computer floor? I have a 200 amp printer to feed. 208 3phase. Type SC cable.
Thanks, Sparky 56

That's one heck of a printer. What are they printing money?

Check out NEC 08 table 645.5
 